Dear all,
In our site, we have 12 flame detectors(IR type) connected directly to plc (direct wire for each detector).we will add another 12.
My question is if we connected them to junction box and then connect them to plc right or wrong. If there a standard determine how to connect the wire (directly or through junction box) and what is this standard.
 
What kind of flame detectors? What kind of PLC inputs?

If you're talking about discrete inputs from a flame detector relay, then terminating the wires in a junction box isn't a problem.
 
The flame detector is IR 3112 general monitors.the plc card is digital input 1756-IB32.and if there a standard determine weather i connected it directly or to junction box.
 
Dear shkoko, from what I recall using a junction is not a problem, but be aware of the length of the wire. The signal can be lost if the travel distance is greater than 100m. Have a nice day!
 
Using Junction Boxes have there positives and negatives. What you do really depends on how you want the system to work.

The positives are you can change where the signal terminates easier. The transition from conduit to tray cable is easier with a JB.

The negatives: Longer cable runs. Most of the time this isn't a issue, especially for digital signals. Analog signals can be affected by the longer cable runs. Another issue is with more connections also comes more points of failure. Many times I have chased down a problem only to find a loose terminal in a JB that is causing all the problems.
 

Similar Topics

Dear all, Good day, Please help me as i have fl4000h general monitors flame detector and i want to connect it to AB plc. This flame has the two...
Replies
1
Views
1,810
Dear, I was looking at a project where they are having a 33meter diameter and using a UV/IR flame detector, this flame detector is covering...
Replies
5
Views
2,572
Dear All, I need to interface fire detector (Smoke, Flame , manual call point, sounder, solenoid and beacon etc) with Allen Bradley Control Logix...
Replies
5
Views
9,577
I have an application where I want to use a safety relay in combination with a flame detector as the sensing element. The flame detector has relay...
Replies
23
Views
1,108
Dear, i was wondering if somebody came accross a code or standard such as from NFPA that requires the use of Flame Detectors for Gasoline, Gasoil...
Replies
6
Views
4,618
Back
Top Bottom