Dear All,
I have a project with PLC 5/80C controller with controlnet. The project contains several analog input flex modules 1794 series. I did not find any BTW or BTR instructions in the ladder logic. but there are N files in the project which might have programmed to have analog values converted into integers.
The issue is I want to install an analog module as well as modify the installed analog module to the PLC. The only software which we bought is RS Logix 5.
Do I require to purchase any additional software to modify and install the present setup?
I had tried in searching net and I found RSnetworx software but I am not sure.
Advance thanks to all.
RSNetworx for ControlNet software, part number 9357-CNETL3, is required to edit the I/O configuration and schedule for PLC-5C15 controllers.
It is vitally important that you determine if you have a very old PLC-5C, with "Phase 1.25" ControlNet, or a PLC-C15, with "Phase 1.5" ControlNet.
The early Phase 1.25 controllers were configured using 6200-PLC5 DOS software, or later with RSLogix 5 itself. The largest user of Phase 1.25 controllers was Solar Turbines.
Dear Ken,
Do you mean I can edit with RSLogix 5? But i have tried almost every option in that software, I didn't find the solution.
If you have a very old PLC-5C, with "Phase 1.25" ControlNet, or a PLC-C15, with "Phase 1.5" ControlNet.
How do I know which phase?
If it is possible with RSLogix 5 then can you post screenshot?
Regards,
drspanda
The processor type is printed on the business end of the CPU module (Example PLC5/40C 1.5 or PLC5/20C 1.25).
You could also retrieve the type from the RSLogix 5 application file Controller Properties folder, General tab, within the "Processor" place holder.
If working on a 1.5 CNet PLC 5 you cannot edit the ControlNet network configuration/scheduling using RSLogix 5.
As Ken stated, you will need RSNetWorx for ControNet (see atachment).
It is 1.5....
I have found it to be 1.5 from Controller Properties folder, General tab, within the "Processor" place holder. Now please guide me whether I need RSNetworx or RSLogix 5?
If RSLogix 5 is sufficient just guide me how to edit analog I/O card related inputs.
Thankyou very much for supporting.
You need RSNetworx. ControNet doesn't use BTR/BTW like the old RIO protocol did. Instead, RSNetworx configures the Remote I/O image table and scheduling of message transfers.
I am doing a PLC5 to Controllogix upgrade (not using conversion software) I hooked up the 1756-DHRIO card to the existing (and working) Remote...
2,778
Good morning, I'm setting up some analog FLEX I/O modules for the first time. I have some 1794-IE8's and some 1794-OE4's. They are in a rack...
3,960
Hi all. I have 1793-IE4 (4)analog inputs modules in a 1794-ADN IOFlex DeviceNet Rack. I cannot find if I can I have access to individual channel...
34
Hi, We have a bag in box machine with a few payoffs that unroll foil. The inverters are PowerFlex 525 and the tension rollers mechanism is...
804
Hey guys, We recently picked up a new customer that just finished a controls upgrade with some other systems integrator company. They upgraded to...
1,771