Hi,
We have a bag in box machine with a few payoffs that unroll foil. The inverters are PowerFlex 525 and the tension rollers mechanism is being moved by pneumatic cylinders - one from each side. A smc analog sensor is mounted on one of the pneumatic cylinders. The sensor gives feedback to the inverter using a current signal - 4 - 20 mA and there is a digital output signal that runs the inverter.
The logic is as follows when the machine is pulling foil the cylinder of the the foil tension rollers mechanism are retracting therefore they give feedback and a run signal to the inverter to run and unroll some amount of foil. There is a hysteresis zone on the sensor that gives the current signal according to the current position of the cylinder piston.
The sensor feedback signal goes in as a process value for the PowerFlex 525 internal PID that controls the frequency of the inverter. The frequency setpoint is in a parameter - A464 for PID 1.
The problem is that after 10 machine cycles or more, approximately 4.4 seconds each cycle, the payoff inverter gives an error - F006 - Motor stalled.
This behavior is observed when the foil roll is getting small i.e. 20-30% of the initial amount.
Best Regards
Konstantin Kolev
We have a bag in box machine with a few payoffs that unroll foil. The inverters are PowerFlex 525 and the tension rollers mechanism is being moved by pneumatic cylinders - one from each side. A smc analog sensor is mounted on one of the pneumatic cylinders. The sensor gives feedback to the inverter using a current signal - 4 - 20 mA and there is a digital output signal that runs the inverter.
The logic is as follows when the machine is pulling foil the cylinder of the the foil tension rollers mechanism are retracting therefore they give feedback and a run signal to the inverter to run and unroll some amount of foil. There is a hysteresis zone on the sensor that gives the current signal according to the current position of the cylinder piston.
The sensor feedback signal goes in as a process value for the PowerFlex 525 internal PID that controls the frequency of the inverter. The frequency setpoint is in a parameter - A464 for PID 1.
The problem is that after 10 machine cycles or more, approximately 4.4 seconds each cycle, the payoff inverter gives an error - F006 - Motor stalled.
This behavior is observed when the foil roll is getting small i.e. 20-30% of the initial amount.
Best Regards
Konstantin Kolev