Im trying to add a remote rack to a plc with a 1756 controller

i like to use flex I/O as the remote rack for space resons but dont know how to add it to the prodject
the flex I/O modules do not excist in the list of avalible modules to use but reading manuals it seams i should be able to use flex I/O

nowhere can i find how to add the moduels to the prodject so if anybody knows how or if its posible please let me know

Hans
 
What communication protocol are you using? Ethernet I/P? Do you have a ControlLogix Ehternet card defined in your project? Then under that card you should be able to add a Flex I/O Comm card.
 
How are you planning on connecting to the Flex I/O? Ethernet? If so you should be able to find the 1794-AENT listed in your available modules.
 
im using ethernet/ip

one thing i dont understand is that if i use a compactlogix controller i have alot of options when it comes to moduels like vfd,s ,flex I/O and so on

if i try control logixs i only get moduels that has 1756 as a name
no vfd,s, no flex I/O,s
 
When you select a CompactLogix, the Ethernet module is already built into the controller so the Ethernet "branch" is already on the "I/O Tree".

When you use a ControlLogix, the Ethernet modules can go in any slot of the chassis, so you have to insert an Ethernet module like a 1756-EN2T into the IO Tree.

Once you do so, you will see the Ethernet network object, and you will be able to right-click and insert and see the network devices you want, including the 1794-AENT and 1734-AENT/AENTR (for POINT I/O).
 
Thanks Ken

that whas very helpful .im using a plc that in the shop for training to learn how to set this up before i do the real change.

on the trainer the ethernet card is 1756 enet/a ethernet when i right click it the option to add new modules is greyed out

on the actual prodejct i can right click and add new mouels inc flex I/O

not sure why the trainer plc wont let me add a new module. Do i need to change the card on the trainer?

Hans
 
The 1756-ENET Series A was the very first ControlLogix Ethernet module, released in 1997.

The Series A never supported I/O over Ethernet; it was only for gaining access to the ControlLogix backplane and bridging messages to other networks.

The 1756-ENET Series B supported I/O over Ethernet, but it has far less capacity than the other modern 1756-ENBT, 1756-EN2T, etc.

Examine the product sticker on the side of the 1756-ENBT module. If it is a Series A module that shipped from the factory with version 1.18 firmware, then it can be flash upgraded to Series B firmware.

If it shipped from the factory as version 1.16 or earlier, it cannot be upgraded.
 

Similar Topics

Hey All, I'm currently building a control system for a large building in a industrial setting. Doing lighting, vent, roof control, door access...
Replies
12
Views
3,504
I thought I remembered a forum post here asking this, but either I was mistaken or the search terms are too vague and I can't find it. I have a...
Replies
7
Views
7,079
Just pulled my first AB Powerflex 525 Drive out of the box and set up the IP address using Connected Components Workbench. My goal is to be able...
Replies
14
Views
4,678
I have an application with a rack of flex i/o on RIO My issue is I am set up for 4-20 mA input. my measurement device when at stand still...
Replies
8
Views
3,224
I use PLC 5/40 and try to use Flex IO as a remote IO with 32 point IO modules. Flex layout is show below 1. 1794-ASB/E 2. 1794-IV32 3. 1794-OV32...
Replies
8
Views
6,016
Back
Top Bottom