for instructions on how to debug message "System Configuration mitmach"

codientt

Member
Join Date
Aug 2010
Location
ha noi
Posts
8
I am currently using PLC's CPUE05 versamax GEFANUC, I get an error "system configuration mitmach" but could not overcome. Although I've replaced the CPU and the CPU module is in error and new modules, but they are still on the error.

Hope you help me how to fix this.
 
Compare the configuration found in the software with the actual configuration of the PLC. Look very close at any module that may have jumpers or DIP switches such as analog I/Q, the jumpers must agree with the software to make the configuration equal.
You can find details for the I/Q modules at the GEIP support web site.
 