freeport for Siemens s7-200
When you are using freeport communication mode on Siemens S7-200 , once you got enabled the freeport mode changing the configuration, How can we go back to the PPI protocol in order for us to have communication with the PLC again?
I don't know if you have the manual for the S7-200, but in appendix D (regarding Special Memory Bits) it is described how to use the position of the mode switch todo this. I have once used this and in my program there was a subroutine to do this. This is the listing of this routine:
NETWORK 39
SBR 0
NETWORK 40
//Stop/Run/Term switch in term position:
//-reset comms, put port in PPI mode, detach and disable
//interrupts
LDN SM0.7
O SM0.1
MOVB 16#C8, SMB30
DTCH 8
MOVB 0, VB516
DISI
NETWORK 41
//Switch in Run position:
//-initialize freeport mode, enable interrupts. Needs to be
//one-shotted so that ISR0 can detatch itself when complete,
//and attach ISR1
LD SM0.7
EU
LD SM0.7
A SM0.1
OLD
MOVB 16#49, SMB30
ATCH 0, 8
ENI
NETWORK 42
//51h=2400 baud
//4Dh=4800 baud
//49h=9600 baud
//45h=19200 baud
RET
Kind regards,
The "Free Port Mode" is part of the program running and accessing one of the ports. You can use the second port for PPI or put the mode switch in the STOP postion and then back to the TERM position to control from the software.
This will disable freeport and turn it back to PPI when the switch is in 'TERM'
  SM0.7           SM30.0
This is for port 0. If on port 1 use SM130.0 (I think)
Paraffin power,
that's OK if and only if you're using the same baudrate and the same bitframing on both freeport and MPI. If that's not the case, see my previous post, which deals with all settings.
Kind regards,
Thanks & another questio
jvdcande said:
Paraffin power,
Kind regards,
Hello guys, I know another freeport question.. I am trying to set up communication between via a rs 232 digitizer to PLC. I am using hyper...
2,047
Background: Using a S7-200 to talk to a Mettler Toledo Weight Controller. The comms is RS-232 serial. I have done this with an AB Micro Logic...
8,910
Hi There I need to write the current DateTime to a printer on Port0. Any quick way of doing this without having to convert BCD-to-Int and then...
1,725
Dir sir! I am using citect scada v5.50 and S7-200,cpu 215.Via PC/ppi cable ,i want to use citect to control that PLC,do i use freeport mode in...
3,886
:) Hi there can anyone answer me about freeport in s7-200?? does it send just standard ascii characters? 🤞🏻 or is it like ppi (has some...
2,229