Hi, a customer has an installation on which a Yamatake DCS monitors about 60 Rosemount FF temperature transmitters. The DCS is a Mobdus RTU master and in between the FF field devices and the DCS the customer has a Rousemount 3420 FIM (Fieldbus Interface Module).
The 3420 FIM has been discontinued years ago and the customer is thinking of a replacement, either with Softing's FG-200, or with a Yokogawa Stardom system (which seems to be kind of overkill, I mean using a Stardom DCS as a Modbus to FF gateway to yet another DCS).
In terms of cost and space, the FG-200 seems to be the right choice, but the customer's 3420 FIM's project was poorly documented by the Emerson system integrator, and the end-user has no control engineer with FF knowlegde. For them it is basically a black box. Hence they expect my company to do the engineering as well, not just supplying the FG-200.
I am familiar with FF technology, the FG-200 and the configuration tool for FG-200, but never have setup an actual system, just demos and simple customer trainings. The actual system is only monitoring temperatures and no valve positioner or any actuator device is being used. So, fortunately, for the commissioning it would be acceptable to have some communication interruptions, but here is the doubt I have, and would be grateful if someone familiar with the 3420 FIM could provide some advice.
The 3420 FIM is the LAS (link active scheduler) and I do not understand very well the rest of the configuration. I have received some screenshots of the system. What I want to know is whether I can configure the FG-200 with the same function block application that the 3240 FIM has, so that say I disconnect segment 1 of the 3420 FIM and connect it to the FG-200's segment 1, then do some testing and then, I really need to know, if I reconnect FF segment to the 3420 FIM, whether "the original system would continue working normally". I have this doubt because in the case of the FG-200, it is necessary to configure the function block application, and download the configuration to "both", the FG-200 and the field devices. But I don't want to change anything in the field devices with the Softing tool, lest the field devices became unable to communicate to the original system. So I am thinking to download the configuration only to the FG-200, without the field devices connected to the FG-200. Of course the configuration tool will say that it cannot download the configuration of the field devices, because of course they are at this point not connected, and a lot of errors will show-up in the log, but I think (although I an not 100% sure) the function block application should be configured in the FG-200.
Once the configuration is downloaded to the FG-200, I would disconnect the segment from the 3420 FIM and hook-up the FG-200, then use the MBPOLL tool to verify the process value, the built-in web server and the configuration tool itself to try to check process values and so on. But if after reconnecting the field devices to the old 3420 FIM the system does not reestablish operation, that would be a disaster.
I am so concerned that I may hire an Emerson engineer to be with me during the commissioning so that he can fix anything I screw-up, and if the customer says they do not want to pay for the Emerson engineer, then I will wish them the best of luck with their endeavour.
Anyways, thanks for reading down to this point, and if you have advice, it will certainly be most welcome.
The 3420 FIM has been discontinued years ago and the customer is thinking of a replacement, either with Softing's FG-200, or with a Yokogawa Stardom system (which seems to be kind of overkill, I mean using a Stardom DCS as a Modbus to FF gateway to yet another DCS).
In terms of cost and space, the FG-200 seems to be the right choice, but the customer's 3420 FIM's project was poorly documented by the Emerson system integrator, and the end-user has no control engineer with FF knowlegde. For them it is basically a black box. Hence they expect my company to do the engineering as well, not just supplying the FG-200.
I am familiar with FF technology, the FG-200 and the configuration tool for FG-200, but never have setup an actual system, just demos and simple customer trainings. The actual system is only monitoring temperatures and no valve positioner or any actuator device is being used. So, fortunately, for the commissioning it would be acceptable to have some communication interruptions, but here is the doubt I have, and would be grateful if someone familiar with the 3420 FIM could provide some advice.
The 3420 FIM is the LAS (link active scheduler) and I do not understand very well the rest of the configuration. I have received some screenshots of the system. What I want to know is whether I can configure the FG-200 with the same function block application that the 3240 FIM has, so that say I disconnect segment 1 of the 3420 FIM and connect it to the FG-200's segment 1, then do some testing and then, I really need to know, if I reconnect FF segment to the 3420 FIM, whether "the original system would continue working normally". I have this doubt because in the case of the FG-200, it is necessary to configure the function block application, and download the configuration to "both", the FG-200 and the field devices. But I don't want to change anything in the field devices with the Softing tool, lest the field devices became unable to communicate to the original system. So I am thinking to download the configuration only to the FG-200, without the field devices connected to the FG-200. Of course the configuration tool will say that it cannot download the configuration of the field devices, because of course they are at this point not connected, and a lot of errors will show-up in the log, but I think (although I an not 100% sure) the function block application should be configured in the FG-200.
Once the configuration is downloaded to the FG-200, I would disconnect the segment from the 3420 FIM and hook-up the FG-200, then use the MBPOLL tool to verify the process value, the built-in web server and the configuration tool itself to try to check process values and so on. But if after reconnecting the field devices to the old 3420 FIM the system does not reestablish operation, that would be a disaster.
I am so concerned that I may hire an Emerson engineer to be with me during the commissioning so that he can fix anything I screw-up, and if the customer says they do not want to pay for the Emerson engineer, then I will wish them the best of luck with their endeavour.
Anyways, thanks for reading down to this point, and if you have advice, it will certainly be most welcome.