FT View SE with a Schneider PLC

Join Date
Jun 2005
Location
Montreal, Quebec
Posts
252
Hi All,
Does anyone here have any experience connecting a Schneider M340 PLC with FT View SE? I have a new system (current version) where there is a 3rd party supply of a Schneider PLC for a sub system. The rest of the system is all ControlLogix PLC's.

I am wondering if I would be better off to switch to a 3rd party SCADA softwart that is used to connecting to different PLC manufacturers like iFix or Wonderware. Also, does SE have direct drivers or should I go with an OPC interface...

Any feedback is appreciated.
 
Does FT view have a Modbus or ModbusTCP driver (I would be surprised if it didn't), if so just use this to connect straight to the M340. The RJ45 port on the CPU with a black arrow next to it is the Modbus port, if the CPU has ethernet it will be the RJ45 connector with the green arrow next to it.
Another approach - you could add a NOC module to the M340 and then it will have an Ethernet/IP interface.
 
Last edited:

Similar Topics

Has anyone ever used Schneider's OPC Factory Server with Rockwell's FTview SE Local station before? I'm using a Schneider 416NHM30042A Modbus Plus...
Replies
0
Views
1,515
Hello all, Currently a Magelis touchscreen running Vijeo talking to a CompactLogix. I'm hoping to switch out to a 15" Panelview running FTV ME...
Replies
3
Views
3,112
i have 2 backups: *.PVC and *.pvd file types thanks in advance for any help
Replies
4
Views
67
Has anyone found information on using the variable message file? I keep looking for documentation on how to implement the message file name as a...
Replies
0
Views
41
I'm at a loss here and hoping someone else has seen this: Background: We've got two identical machines on our floor (we'll call them machine A &...
Replies
0
Views
62
Back
Top Bottom