G306 HMI to Unidrive SP comms
Hi
All suggestion thus far have all been valid. I would also go back and check all the tag values in the HMI to ensure you are not writing to the registers for the communication protocol.
Just A Suggestion
Tom
I loaded tmporary program that reads only one parameter from the drive. So eliminated that.
Been crook for last few days so no work on the problem. How ever I'll try to leave conerter in the circuit or use 232/485 converter and use 232 port on hmi if that does the trick. But I'm sure that it ia down to signal level. Pure electronics.
The suggestion to include terminating resisters is probably the best one. Another option might be to add to signal isolator like the B&B Electronics http://www.bb-elec.com/Products/Ser...y-Isolated-RS-422-485-Repeaters/485OPDRI.aspx
This is just an option, I think the resistors *ought* to fix your problem.
node to node or port to port
3 drives are connected to each other with all pins via a splitter
1-1-1
2-2-2
3-3-3
Etc.
One port from splitter is cable going to hmi. Pin 2 to pin 7 and pin 7 to pin 2. Splitter is basic 5 port spliter 1 to 1.
mind you this is original setup in the machine. Since then i tried various combinations. With pins 2 and 7 only. With /without splitter. With / without ground pins. With / without terminating resistors. Always the same result.
Hmi is the master for drives comms. There is no problem with plc comms. It is on different port tough and doesn't use modbus for comms with plc.
The manual says that it has to be daisy chained, not star, and that it requires terminals 2,3,7. are you connecting to those terminals?
BTW, I have my doubts that the splitter will work, if it is the kind I am familiar with it is more like a star network.
You are right. But this machine was working for 10 years with described setup. I have also tried daisy chain with no luck. Don't forget that unidrive doesn't communicate even when connected just to hmi,without other 2 drives. So star / daisychain really is not relevant yet. I have tried connecting ground pin as well. No difference.
Not sure where to go with this, sorry. Not that it helps you, but I've daisy-chained 30 Modbus devices to a similar Redlion device without even terminating resistors.
You could try the isolator I suggested before. I've never needed it for Redlion equipment, but have needed it for other Modbus Masters.
I am using a MicroLogix 1100 of AB which going to read data from HMI G306 of RedLion. I'm using this HMI like a Gateway and the comm protocol that...
10,547
Hi everybody, I am working on a project where the G306 HMI is set-up as a Modbus Master where it is collecting data from 7 analog panel meters via...
11,854
Happy New Year everyone, I am working on a Prototype project using a AutomationDirect Click Ethernet PLC and a Red Lion G306 HMI. I have the HMI...
1,728
So i have this application where I have to read/write from/to the serial port. Write has worked fine so far, but it is reading that I have issues...
1,883
Hello Everyone, I have been playing with the Automation Direct Productivity 2000 PLC for the past couple days. I have a program in the PLC now...
1,871