Dear Fellows;
Good day. Here i share two images one is PLC Sweep Time control and Monitor Screen and the other one PID Control Screen.
First i define the problem. The Program control the fuel of the Gas Turbine but when we start the turbine it is not stop at the given set point and speed overshoot and tripped.
In PLC Sweep time i think it is the scan time in GE 90-30 am i right?
If you see the image the actual sweep time of the program is 14 mSec while it set to 100 mSec. In my point of view that PID sets its parameters CV after 100 mSec?
In the Second Image the detail of PID i want to understand that
1. If i change the Upper clamp value from 32000 (20 mA) to 18000 then CV not going to beyond 18000 and limited to this value regardless how much error (SP-PV)?
2. Near the bottom of integral value there is a 32000 value appear it means the SP and PV are compared in Counts or can i say that SP (%R) and PV (%AI) are in counts. Is it god technique to calculate the error by counts or convert counts to EU (Frequency for speed sensor) for calculate error?
3.The sample period is 10 mSec is it correct value according to Sweep time?
4. Can i fix the Sweep time that program must scan in 25 mSec instead of 14 mSec because the fuel control mechanism is Electro Hydraulic (Response time is slow) ?
5.I want to understand Dead band +/- , Bias, and slew time?
6. Can i change the Ki (Proportional) by using the Move instruction at different speeds like
If speed between 35 to 55 then update KI is 8.0,
If speed between 55 to 62 then update KI is 6.0
and so on?
Regards
Regards
Good day. Here i share two images one is PLC Sweep Time control and Monitor Screen and the other one PID Control Screen.
First i define the problem. The Program control the fuel of the Gas Turbine but when we start the turbine it is not stop at the given set point and speed overshoot and tripped.
In PLC Sweep time i think it is the scan time in GE 90-30 am i right?
If you see the image the actual sweep time of the program is 14 mSec while it set to 100 mSec. In my point of view that PID sets its parameters CV after 100 mSec?
In the Second Image the detail of PID i want to understand that
1. If i change the Upper clamp value from 32000 (20 mA) to 18000 then CV not going to beyond 18000 and limited to this value regardless how much error (SP-PV)?
2. Near the bottom of integral value there is a 32000 value appear it means the SP and PV are compared in Counts or can i say that SP (%R) and PV (%AI) are in counts. Is it god technique to calculate the error by counts or convert counts to EU (Frequency for speed sensor) for calculate error?
3.The sample period is 10 mSec is it correct value according to Sweep time?
4. Can i fix the Sweep time that program must scan in 25 mSec instead of 14 mSec because the fuel control mechanism is Electro Hydraulic (Response time is slow) ?
5.I want to understand Dead band +/- , Bias, and slew time?
6. Can i change the Ki (Proportional) by using the Move instruction at different speeds like
If speed between 35 to 55 then update KI is 8.0,
If speed between 55 to 62 then update KI is 6.0
and so on?