I have a problem using AD DL-05 (AC power, DC input and output) with an analog module F0-04AD-1. The PLC locks up itself once a while. The operator has to cycle the power to reset the PLC. The DC was designed floating. But recently I realized that the analog module internally short its current input – to the PLC G and LG. So DC and AC are grounded together. I suspect this is reason the PLC got locked up. I have a line filter for the AC before DC power supply and the PLC. Now I disconnected the G and LG from line ground to make both AC and DC floating. It seems to me that it is not right to leave the ground not connected for the PLC AC power. But it works fine so far. Is there anybody who can tell me if this is right way to do it? Or any other recommendation to solve my problem?