One thing I suggest is take off the tick on the FX communication setting, the BD board defaults to MC protocol if the PLC System 2 is left unchecked, re-boot the PLC and set your baud to 9600, Even,7,1 on the HMI this is what you do on other HMI's. This will test if the cable is ok with the default parameters.