can i connect a rtd transmitter which is working using HART protocol ...can i give input to micrologix series plc or does it require special type of input module for hart sensore??:unsure:
 
A regular 4-20mA input will handle the HART 4-20mA output as just a 4-20mA signal, but a regular 4-20mA input won't be abel to decode any of the additional HART data.

If there's some requirement to use a HART communicator (handheld or software) to configure the HART field instrument then those devices need at least 250 ohms in the loop circuit to be able to read the HART signal.

Sometimes an additional resistor is put in series in the circuit for those analog inputs that use 10 or 100 or 62.5 ohm resistors (or whatever) across the AI input for current signals. Others break the loop open, insert a temporary resistor to do what's needed when they have to use the HART communicator or HART modem, then put it back together when they're done.
 

Similar Topics

Does anyone know of a HART communications module for Allen Bradly Micrologix I/O 1762 type modules. Found ones for 1769, and 1734 from Spectrum...
Replies
4
Views
2,027
Hello I would like to have suggestion for a nice hand held programmer. Hopefully battery powered easy to work with at a decent price. I've seen...
Replies
5
Views
2,442
Hi every body Can any body help me for information on the following 1)HART protocol 2)Any good refernce e.g. book on the instrumentation fault...
Replies
7
Views
4,536
I would like to install a non HART device in a system that uses HART, do you have a converter
Replies
1
Views
106
I am going to need to use HART multi-drop in order to handle a series of Vega Radar units. There are a lot of options and I'm wondering what...
Replies
3
Views
271
Back
Top Bottom