Heartbeat between iFix HMI and Allen-Bradley PLC
golftmd13
Feb 2018
Missouri
I was wondering if anyone knew a way to go about creating a heartbeat between a PLC and an iFix HMI screen so that you can see when the PLC is out of run mode.
I'm sure there's more than one way to go about doing it, any input is greatly appreciated.
I did something similar on a tablet HMI that loses comm's.
I just put a flickering (2 seconds on/2 seconds off) bit for the HMI to read and use that as a visibility bit on the HMI. If it ever stays off or on longer than 4 seconds the comm's have been lost.
I am not very experienced in iFix, but if it has timers built in you could watch a flickering bit that runs two timers and if either timer get done show a comm's fault.
I run a 15 sec timer in plc logic. I monitor the elapsed time register in HMI. Then when elapsed time reaches 10 sec, I write "0" to timer count. PLC has alarm if timer times out.
In studio 5000 is there an easy way to do a Heartbeat between two Control Logix PLCs? Say you have Produced and Consumed from both is there even a...
1,222
Hi I need to set up a comm loss heartbeat between a Siemens s7-200 226 plc (Slave) and a Siemens s7-300 314c-2dp PLC (Master). They are...
3,145
Hi everyone, I have a task at work that I'm hoping someone will be able to help me find a solution for. Here is the background info: I have a...
417
Hi everyone I've created an FC that includes the blocks TCON, TDISCON, TSEND and TRCV. This block has to be as generic as possible across...
1,522
Hi all, I have an application where there is a Control Logix PLC connecting to a B&R remote I/O station over Modbus TCP via a prosoft MNETC...
1,911