Help ET200X Siemens

Join Date
May 2002
Location
Varese, Italy
Posts
23
I have a problem with Siemens CPU 315-2DP with 2 ET200X conected, when I go in stop and next in Run on PLC on ET200 and PLC there is the led Bus Fault ON, to resume I must shunt down power supply.

Someone has a solution for this problem?

Thanks for Help
 
Siemens

Do you have expansion i/o via profibus? If so chances are one of those
modules has failed. Describe complete system and maybe we can help.
 
Luca,

You have probably already checked, but:

1 - Make sure your hardware profibus addresses agree with the addresses in your hardware configuration.

2 - Check your wiring (red to red, green to green) :)

3 - Make sure you have terminating resistors on both ends of the profibus network.

Good Luck -
Kevin Hammond
 

Similar Topics

HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
Replies
7
Views
146
I have an old Sentry Palletizer (S/O Number 3007 / Serial Number 1172) that has lost its program as the backup battery died years ago. I can...
Replies
0
Views
106
Hello, I need to write the following program in Ladder language, but I could not integrate the Fibonacci sequence into the ladder. Can you help...
Replies
22
Views
472
this a program to send data to barcode printer I want to integrate a new printer in a new machine and i wanted to adapt the old prgram on it but I...
Replies
4
Views
176
So i've been at this for a long while, i have Citect Scada 2018, i have full access to everything but i can't seem to find any option or...
Replies
0
Views
68
Back
Top Bottom