Earlier you noted the driven equipment is a dyno. I am assuming that this is a test cell and being a two shaft engine it will drive a generator eventually. If this is true I think you are well in good control at 1%. For example if you are in island mode(stand alone gen set) 1% is fine. Plus in droop mode you will droop the freq by maybe 10% based on the load. If you are syncing to a larger system you will be coupled electromagnetically through the generator. The power turbine will run at the system freq(gearboxes ....). That is way over simplified but you get the idea. If this is a compressor or pump application then I still think you should be fine. PCD is an indication of the engine performance. If you try to open the fuel valve too quickly you could upset the engine. By knowing the PCD you can limit the fuel valve from opening too much. Its been some years since I worked on an old Saturn. The item you mentioned above that takes PCD and maybe fuel pressure is possibly a proportioner that limits the valve based on inlet fuel pressure and PCD. Not sure Though. Anyway you can just make an array in the PLC and use it like a look up table, or do a calculation. Basically if the engine is at idle the PCD is low and you don't want to dump a bunch of fuel into it. Another example would be if you were running on load and the load increased because someone started a motor. The PID is going to respond by increasing the fuel flow. If it takes a while to respond the reset windup will cause the fuel valve to continue to open. By not considering the PCD you could cause the fuel mixture to richen up and eventually stall the engine. Many situations like that.

Hope this helps.
 
Last edited:
Hi;
Yes i am working in TEst Cell and here we tested the engine Centaur 40 family the skid and data aqusition also with control get from the Solar turbine. But for saturn 1100 the skid is got from third party ELBAR. Now i recently join the company and change the control from relay logic to PLC. We used SCHENCK D1100-2E low speed dyno with gearbox 4.051:1 ratio.
Can i ask what about you and are you still working in Solar turbine?
Can we communicate on gas turbines to exchange knowldge and usefull discussion. Can you give me your email ID?
Do you understand For test cell 1% is acceptable?
regards
 

Similar Topics

Dear all, I have a problem tuning a PID loop. I am trying to control the temperature of a pasteurizer for beer cans and bottles. I am using S7-200...
Replies
8
Views
4,174
Hello, I have a problem with tuning my PID loop in my RS5000 project. In my program I am using a PID loop to control the KW output of an engine...
Replies
11
Views
4,309
Hi, I'm new here and horribly inept in working with Step7 and i have a problem. I am trying to use PID control on two analog valves in order to...
Replies
2
Views
1,703
Hi experts; I have Ge 90-30 CPU 352. I use PID (ISA) and first set only the proportional and setting as under; Error term= SP-PV Upper clamp=32000...
Replies
4
Views
2,049
dear all: we have a automated vehicle which runs on a magnetic tape. we are taking analog input [0 to 10] volts from a reader this has a...
Replies
3
Views
3,689
Back
Top Bottom