Help on Lantronix UDS-1100 IAP - Modbus Gateway
harryting
May 2002
Puget Sound
2,595
Old thread: https://www.plctalk.net/qanda/showthread.php?t=114187
I have configured many other gateway before but I can't figure this out. It seems they are missing some documentation.
Have the device on hand, already updated the firmware to the "modbus" version and now am lost on what to do next. Typically, there's a database cross-ref function but I can't see it anywhere.
Background: Old: 4 modbus slave devices on RS485, connected to PC with 485/232 converter. Application side is Kepware - Modbus RTU. This setup works.
New: same slaves going to Kepware but via Modbus TCP. Trying to use UDS-1100 as the gateway.
Reading between the lines, I figured out that the Lantronix works a bit different than other gateway. It doesn't have a cross-ref table but rather just pass things on and use the modbus device ID on the TCP side.
Still figuring out the rest though. Can't get a response yet and I haven't found a way to troubleshoot the TCP independently from the serial side, unlike other gateway I dealt with in the past. Any suggestions?
Also, this is UDS-1100-IAP with the Modbus firmware.
It sounds like that it converts serial to serial over TCP. It is different than Modbus TCP.
On kepware you still need configure serial modbus driver and then select ethernet encapsulation.
I think that only applies if it's using the standard firmware, instead of the "modbus firmware". However, it's easy to try so I'll report back.
this a program to send data to barcode printer I want to integrate a new printer in a new machine and i wanted to adapt the old prgram on it but I...
69
50
Hi all, hope you are having a great day, I am in need of your help to create a AOI or program that does this kind of job: I have a IO Link...
24
420
please help me . I have to make this ladder diagram and I can’t figure it out :(
359
Hi Everyone, i was hoping for a little help with this module. i have data that needs to be read from a different plc through the Modbus plus...
237