Ieta,
Never fear, I have fixed it to do as your described.
However, this does not mean that I agree this is a good way to start a bunch of motors. For example, for many similar projects that I have done where large motors (20 horsepower or larger) start in sequence, if I did not allow a time delay of 5 to 10 seconds for each motor to get past its large starting current before the next motor was allowed to start, then bad things happened:
A large KW Demand charge appeared on the electricity bill, main breakers got overheated and tripped out, motor starters tripped or burned up from high start-up currents, the plant owner ran around shouting, waving his arms and pointing fingers, and my boss gave me a butt-chewing.
If these are small motors, no problem. If not, I suggest a START-UP timer in addition to the SHUTDOWN timer.
Also, I guess this may be homework. If so, may I suggest that you add a STOP pushbutton with logic to STOP motors. That should be your first worry: how to shut down things that are turing at high speed and can catch loose sleeves and pull people into open mixers. If that happend, where is the big STOP button to shut this stuff down.