We have an analog input-module who has a fault. Now, I want to read the diagnostic data of this module. I have read the manual on how to call SFC59 in OB82 several times, but can not understand the whole thing.
CPU 318-2DP, S7 V5.1
It is an analog inputmodule with starting adress PIW300.
My questions:
1. REQ= can this always be 1 ? What happens: is he always reading the data or only once if the error rise?
2. IOID = B#16#54 -> OK?
3. LADDR = IW 300 -> OK?
4. RECNUM ???
5. RET_VAL = for example MW804
6. BUSY = M 5.0
7. RECORD = for example MW 806 ---->or is only data type BYTE permitted??
8.What is the difference between the RET_VAL- and the RECORD-output?
9.What can you do with the local dat of OB82?
Lot's of questions, isn't it ;)
If you just need to troubleshoot the module right here and now, just look in the diagnostics for the module in the hardware configuration in STEP7.
By the way, you do look a little bit young to be playing with PLCs :eek:
SFC59???? isn't that for data transfer, i.e comms processors?
For diagnostics you want SFC51 or FB125, although I would use Jespers suggestion. Jesper asked a question on these blocks a little while ago click here for that thread
Paul
OK, but SFC51 is to read out the diagnostics of the DP-slaves, and I want to read the diagnostics of an Analog Input-card.
The error is there for just a little time (0.1ms). In the diagnostics of the CPU ther is only: External module error, channel error detected, external error, incoming event, Event 16#3942.
Now I want more specific diagnostic data by calling SFC59(RD-REC) in OB82.
In the STEP7 hardware configuration, highlight the DP node that has the error (not the CPU !), then select PLC ... Module Information.
That should display status and diagnostics for the particular node.
I believe that the SFC51 will simply provide the same diagnostic information as you can view in STEP7.
But if ther's no error, there is no module information available.
I want to program that I store the information if an error occures. An analog inpu-card is no DP-node, or am I so wrong?
I believe the diagnostics window allows you to browse previous errors.
Edit: I see now that you say it is in the CPU rack. Look in the diagnostics file if there are more messages (one error can generate several messages).
I do not know if you can open a diagnostics window for the analog module. Maybe you can.
Yes, but I want the informaton more specified.
I am using an analog module that supports diagnostics. If this detects an error, it sends a diagnostic interrupt request to the CPU. The OS then calls the OB82. In its local variables, the OB82 includes the logical basic adress and4 bytes of diagnostics information .
I should use SFC59 to read out the channel-specific diagnostics data.
Greet
The penny has finally dropped.. I understand what you are trying to do.
I still stand by my statement that you can't use SFC59 for this, but I do believe SFC51 will do what you want. I have never used this SFC so I can't be much help with setting it up, the Siemens help files will have to be your source of information, we know how helpfull they are....not!
Paul
greet,
maybe you can get additional information about that diagnostics entry with the button "Help on event" in the lower right corner of the diagnostics window.
Dear Greet,
Regarding SFC59
REQ should be 1 for one scan and cannot be again 1 until you'll see 0 at BUSY output.
IOID is ok.
LADDR should be w#16#012C (300 in hex).
RECNUM 0 or 1 however in your case should be 1.
RECORD is output of the SFC and can be as long as 240 bytes of data. You must provide here ANY pointer to large enough area.
You can do the same with SFC51.
Have look at manual "S7-300 Programmable Controller
Module Specifications" Appendix B "Diagnostics Data of Signal Modules". And have nice reading. :D
HI everyone, i am new to Siemens plc programming and i am in need of some help. yesterday we had an S7-1200 CPU 1214C fail to turn on an output to...
90
I have an old Sentry Palletizer (S/O Number 3007 / Serial Number 1172) that has lost its program as the backup battery died years ago. I can...
105
Hello, I need to write the following program in Ladder language, but I could not integrate the Fibonacci sequence into the ladder. Can you help...
22
470
this a program to send data to barcode printer I want to integrate a new printer in a new machine and i wanted to adapt the old prgram on it but I...
175
67