help with Bulletin 22-XCOMM-DC-BASE DSI Communications Kit
realolman
Mar 2009
here
584
I need a crash course in this Bulletin 22-XCOMM-DC-BASE DSI Communications Kit communicating with powerflex drives and sending control "messages" from ladder logic.
I can't seem to find any good explanation of this stuff in the Rockwell stuff.
If someone could point me in the right direction, please
or if you just want to tell me how to do it.... that'd be good too.
thanks
The 22-XCOMM-DC-BASE DSI Communications Kit is being used to network "small frame" Component Class PowerFlex drives via EtherNet/IP or DeviceNet; because of the size of the drive's enclosure, a 22-COMM-E/D adapter cannot be mounted on-board hence the need for an external "mounting kit".
The kit is basicaly a 24 vdc powered DSI (RS485) to EtherNet/IP-DeviceNet converter which provides a panel mounted, accomodating housing for the 22-COMM-E/D module.
thanks for responding
a CompactLogix and a control Logix on an Ethernet network
What I need to do is stop some motors that are on the Powerflex drives
The 22-Xcomm-DC-base is connected to the same network as the Compact Logix and the COntrol Logix... along with other things
From there the drives are daisy chained RS 485
It's logically identical to an ordinary 22-COMM-E mounted on a PowerFlex 40.
With a ControlLogix-family controller, this is configured exactly like an ordinary 22-COMM-E.
With an SLC-5/05 or MicroLogix 1100 or 1400 controller, you need to use MSG instructions to control the drive. This is not the preferred method to control drives with MicroLogix, and it is generally not recommended for novice users.
Forum stalwart Bernie Carlton has a very good, thoroughly-tested ladder logic example for running PowerFlex 4-series drives using MSG instructions over Ethernet. You can search for it, or he may be along presently with another copy.
Hello, I need to write the following program in Ladder language, but I could not integrate the Fibonacci sequence into the ladder. Can you help...
this a program to send data to barcode printer I want to integrate a new printer in a new machine and i wanted to adapt the old prgram on it but I...
126
51
Hi all, hope you are having a great day, I am in need of your help to create a AOI or program that does this kind of job: I have a IO Link...
24
439
please help me . I have to make this ladder diagram and I can’t figure it out :(
359