Help with function block
cncsparky
Dec 2014
Ks
98
CLX L72 v24
I built my first ever function block routine, a totalizer that was requested by our engineering group. With help from this forum, the totalizer is working great!
Next step is to get Ignition to gather the totals to a database once per day.
My thought was to get Ignition to reset the totalizer, then read the old total. Reading the total is not a problem. What is the best way to reset the totalizer?
Ignition could set the totalizer reset bit, how do I get the reset back to zero (0) once the current total is moved to the old total tag?
In ladder, I'd use a condition to (U) the bit. What is the FBD equivalent of an unlatch? Or is there a better way?
If it were me, I would make MyArray[32] and shift the data into this by the PLC, your pointer is based on day of the month, there is a months worth of data as a nice buffer.
I don't know Ignition, but say it's set to log at 00:00 everyday, I would have Ignition set a bit when the log is done, when set, then use the PLC to shift the current total to the array and then reset the totaliser.
If you don't get the logged bit by say, 00:02, then have the PLC do it anyway, you can also set an alarm that the log hasn't logged. You then have a nice buffer in the PLC should the log fail and nobody noticed for a few days and an alarm if the log has failed anyway.
Please see attached file. I need this program in Function Block form but I am totally lost on this. Any help would be appreciated. Thanks!
301
Hi all, I have a HACH sc200 controller with 2 sensors which I hope to connect an M221 plc to via Modbus RS485 in order to display the info on a...
2,271
I have a discrete 2-state device function block set up controlling a motor with 5 i/o. ProgCommand, FB0, FaultAlmUnlatch, Out, and FaultAlarm...
3,138
Hello!!! This is my first post. Im triying to configure a Totalizer function block on RSLogix5000. I want to know the correct parameters settings...
5,575
Ok got an easy one. i have a scaled (4-20) signal scaled with the scl block in controllogix. the scaled output (0-100 tank level %) is used in...
4,669