Hi! Im a newbie to the plc thing and need some help wiring up my "first PLC" :P
ringox1
Oct 2005
Hamilton
Hi! Im a newbie to the plc thing and need some help wiring up my "first PLC" :p
The plc I have is a AB micrologix 1000 it runs off a seperate 24dc supply. I've got all the inputs sorted out. But im concerned about the grounding terminal on the plc its self. Do I wire it upto the power supplys earth which is in turn connected to the mains earthing system. Or do i wire it to the negative part of the powere supplys input as is done in cars?
This is proably a really dumb question but please im just starting :p
It gets connected to the mains earthing system.
In a typical control panel, you have a ground bar that has a single wire to the mains earthnig system and seperate wires to each device that needs a ground. Daisy-chaining grounds is not good practice.
The ground bar is also usually bonded to the panel metal (with bolts/screws and removed paint from the panel subplate)
The MicroLogix 1000 seems to be more sensitive to noise than most; if you can, oversize the ground wire to AWG 14. I haven't found that written down anywhere, but AB's tech support folks have been telling people to do it.
The manual explains wiring: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1761-um003_-en-p.pdf
This picture is a NOTE in that manual:
Hi, after 30 years involved with automation I'm actually writing my first PLC program and am struggling a fair bit. My background is mechanical...
1,900
I picked up a Siemens S7 1200 from a buddy and I want to start fiddling around with it to learn about PLC's. I don't want to spend a lot of bucks...
2,471
Hi Guys I completed a PLC course a few weeks ago and I've decided to build myself a PLC training rig. I'm using an s7 200 as I managed to pick...
3,147
Hopefully I'll have a legitimate copy of RS500 to program micrologix and SL500 series PLCs. A guy in another group is going to mail me his old...
1,842
I was recently given an FMD88-10 and AN20MA-2, in excellent working condition. I'd like to start learning to build PLC's, and just tinker around...
2,314