HMI, GUI, Touch screens, AB Cat# 27119-T12C4D2

tonyyarbrough

Member
Join Date
Feb 2007
Location
Arlington, Texas
Posts
1
I use several AB PanelView Touch screens of various sizes for a GUI into my PLC's I/O's. For an unknown reason, at no specific time interval the 12.1" color PanelView will blank-out to the infamous "Blue Screen of Death". My recovery is to cycle the power to it, and it all reloads, runs fine. I've done the most obvious things like check the power connections, etc. My AB rep is clueless. Any ideas would be welcomed.
 
Last edited:
Check the stability of the power supply. Glitches, solenoid noise, minor drop outs, etc. can cause that. If it's a 120VAC version, ironically, a lot of UPS's will cause that in an industrial enviornment. If it's a 24VDC version, try a local, dedicated 24V supply.
 
Is it using windows as the platform, it sounds to me like windows 98 if it is then is a normal behaivour of windows it is so unstable, try with ab rep to see if they have a linux like version is far more stable plataform to work with and no bsod.
 
rafaelsainz said:
Is it using windows as the platform, it sounds to me like windows 98 if it is then is a normal behaivour of windows it is so unstable, try with ab rep to see if they have a linux like version is far more stable plataform to work with and no bsod.

No, it's not Win98, it's WinCE.
No, there's no Linux Version.

BTW, the part number is 2711P-B12C4D2.

Tony, any other clues? Is it always on the same screen, or does that matter? Are there any custom configs? How are you communicating to what PLC? Firmware version? ...
 
Last edited:

Similar Topics

Hello, I have a Mitsubishi FX3G 14M PLC and a E615 HMI from Mitsubishi/Beijer. I'm using GXWorks 2 to do the programming and I have no problem...
Replies
4
Views
94
Good people of PLCs.net, I am currently working with an HMI that is advantech 1250H, that communicates with a 1769 Compact logix and Currently...
Replies
2
Views
76
Hello all, I know its not good practice to have duplicate destructive bits when writing plc code, but I'm wondering about writing to the same tag...
Replies
2
Views
120
Hi All, As a precaution my company has been collecting copies all the HMI and PLC programs. I have recorded copies of most of our sites...
Replies
0
Views
73
Hello all! So I have one project with a S7-1214 and a MTP1500 "Project1" and one project with another S7-1214 "Project2". Both of these PLC:s need...
Replies
6
Views
112
Back
Top Bottom