HMI to electricity meter ?????
gomond
Sep 2013
Melbourne
Is it possible to use a MODBUS RTU enabled HMI i.e. TouchWIN or the like to query a MODBUS slave energy meter like the ABB submetering units.
I am trying to figure out how to do this and the one thing that does not seem to be on the web are any decent tutorials or examples showing how to use an HMI as a MODBUS RTU Master.
Thanks Heaps if anyone can help.
Greg.
Have a chat with the guys at Remtron. They may have the answer for you
I can see this a possibility.
Greg.
I have recently viewed a presentation of Omron: it describes a NS touchscreen that was master of several MX2 drives over modbus RTU.
I didn't test it, nor have I experience with it, but it might be possible. Can you contact a Omron person?
When any HMI implements Modbus RTU, it almost invariably does so as the Modbus master. The Modbus master is the device that initiates all data exchanges. When the master wants to read data from a slave it sends a "Read" command that tells the slave the starting address and number of bytes it wants. The slave responds with the data. When the master wants to write data to the slave it sends a "Write" command to the slave. The write command includes the starting address in the slave where the data is to be written and the number of bytes of data, followed by the data.
I don't know the details of setting up communications on the HMI you cited, but just treat the energy meter as if it were a PLC. You will need to get the Modbus map for the meter to know the addresses of the data you want to display on the HMI.
139
Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
50
Does anyone happen to know how to install the graphic picture in HMI when I go into blower selection there are no graphics shown not only blower...
73
Does anyone happen to know how to install the graphic picture in HMI when I go into blower selection there are no graphics show not only blower...
101
Hello All, I've been tasked with automating a flatbed press that runs with some pretty extreme temperatures. I've been told it can run close to...
170