Hot Swapping In Et-200s
altaf_hussain
Dec 2006
Faridabad
17
Hi, I am having an issue of hot swapping in ET-200S.
Is it possible in ET-200S any body have an idea?
If yes what software/hardware required for it.
thanks
I have a distributed i/o setup of ET-200S i.e. connected with cpu313-2dp via profibus.If I remove any card from ET-200S rack then my complete bus become faulty.This is my problem.
My client want hot swapping in PLC setup means in online if I remove any ET-200S PLC card from bus then only this card i/o not work and all sysytem will work as usual and If I will again insert this card in online then this card i/o starts working.
If the "complete bus" is faulty (what makes you say this ?), then the plc will not communicate with any ET200 stations and hence it does not make sense for your system to work as "usual".
You haven't mentioned what the CPU does when the bus is faulty.
I know you can change out ControlLogix cards with the rack powered. And I thought that you could not do it with a PLC-5, but a colleague at work...
4,146
I understand that one of selling features of Controllogix5000 is to be able to swap out a faulty module without powering down the PLC or switching...
3,680
Please I need help in converting this configuration to hot swapping / change module during operation...
1,161
I was thinking of just hot swapping this 1756-IT6I in a ControlLogix Rack. Would any of you have any concerns , doing this ? Thanks and have a...
2,779
Ok I have a CompactLogix L20 Controller and have been building some code that takes up almost all available memory on the PLC. My boss keeps...
4,823