If it switches more current than it was designed for, zero.
The question can't be answered without knowing the load. Spec sheet ratings are generally given for purely resistive loads. Inductive loads will reduce the life. Suppression will mitigate the impact of inductive loads.
If you are switching an output so frequently that relay life becomes a concern, you're probably better off with a solid-state output device. If, for whatever reason you really need the contact output, consider a solid state output driving an interposing relay so that when the relay fails it is easy to replace.
If you need one more output and all you have available is a contact output, you can still add an interposing relay. That will give you a relatively small load on the PLC output and the interposing relay will be the more likely point of failure.
No it has worked for at least 5 years and the relay switches 70 times a minute 24/7. I suspect that I am getting some chattering in the contacts that could be causing my issue.
LOL... if my math is right thats 183,960,000 cycles
Its past do and should be changed out, do they offer a transistor (solid state) one? if yes it would be better that the mechanical relay
Do you have an unused output on the card?
I would reprogram the output to another one. At least that would eliminate the relay if the problem continues.
70 cycles x 60 minutes/hr x 24 hr/day x 365 days/year x 5 years = about 184 million cycles.
The relays used in POINT I/O modules are generally rated to mechanically run about 20 million cycles. At full load, the contacts in those relays are expected to serve for only about 100,000 cycles.
A module that's served for that long at that rate should be considered for replacement.
Certainly if you consider "chatter" a possible reason for a malfunction you may wish to investigate a solid-state interface both for performance and longevity.
Minimum 100,000 operations @ rated load.
Probably not more than 20,000,000.
Publication 1734-IN055I-EN Page 23
Let me see now . . .
5 years times 365 day/yr X 24 hr/day X 60 min/Hr X 70 cycles/min = (roughly) 184 Million cycles . . .
I do hope you have a spare one on hand?
Poet.
Are you sure it's 70 cycles per minute and not 70 cycles per hour? Or has the application changed since the original installation? At the risk of insulting the OP, it's hard to imagine a competent designer intentionally using a relay contact output for that application.
At 185 million...I am pretty you have exceeded MTBF of relay components.
MTBF is "Mean Time Between Failure". Most components have this rating.
Good Evening , We have a number of Powerflex 525 Drives . I took notice for years elsewhere and our plant , that our Powerflex 525 drive...
643
Good Afternoon, Just wondering , are many of you using SAP in your plants ? If so , is it difficult to learn ? Are there many training...
1,428
It better to have too many instead of not enough right?
26
2,902
Hi all- I have an application where: - I have a fixed system with a pre-determined, static, network (say, 192.168.2.0/24). - That system...
4,243
I have an application that needs 20 inputs and 20 outputs with only 10 XNOR and 10 NAND blocks. I could do it with relays, but this could end up...
16
5,176