How to access a Codesys pointer via OPC UA
jagjag1
Jan 2012
Codesys
17
I am trying to access the value of a pointer via OPC UA in Codesys. I can share it directly and in a struct but I cant access the value of it when its linked. I have tried to access it via UaExpert and python script but I cant go down the last level.
Trying to access this:
GVL.astItem[1].pIntPointer^
NodeID:
ns=4;s=|var|CODESYS Control Win V3 x64.Application.GVL.astItem[1].pIntPointer
Why not assign the value of the dereferenced pointer to another global variable and refer to that via OPC?
I think L D[AR2,P#0.0]'s suggestion is not only correct, but it is the only thing you can do to get such value from the CODESYS OPCUA server to your OPCUA client.
Your inquiry sparked my curiosity and tried to setup something to see if it was possible. But now I understand why and I may not be able to give you a proper explanation due to both English not being my first language and by virtue of not being an OPCUA developer, but rather I can give an explanation in a more colloquial way. OPCUA technology's purpose is to hide from the client low-level addressing issues in the server. Only process data can be exposed in the OPCUA address space. As you can see in the screenshot below, the OPCUA server is indicating that the data for the pointer is unavailable. Thus, as L D[AR2,P#0.0] says, you need to have in the CODESYS program a variable and assign to it the value in the pointer,
Thank you for the response I found a different way to to it but resulting to more or less the same function and I will share it if anyone will need it in the future.
I tried reading the pointer to various variables with UaExpert, Python and C#(opc.UaFx.Client) in all platforms i could see the variable but when trying to read the value all resulting in bad/invalid data because the opc ua client could not process the pointer. So instead I used REFRENCE TO and all the OPC ua platforms instantly found the variable since the reference does not add an new level to the variable, array or struct.
Simplified example:
VAR_GLOBAL
aiItem : ARRAY [0..50] OF INT;
refiTemp : REFERENCE TO INT;
iPointer : INT;
END_VAR
GVL.refiTemp REF=GVL.aiItem[GVL.iPointer];
Hope this helps someone.
jagjag1, this solution is so very interesting. Thanks for sharing this.
You have helped me remind myself that even though I "think" I know CODESYS, in fact I have so much to learn.
https://help.codesys.com/api-content/2/codesys/3.5.13.0/en/_cds_ref_assignment/
Did not know about the "Assignment operator ‘REF’"
And it works...
P.S. for a person like me it is easier to understand the issue with a little bit more detail.
I like to tack {attribute 'no_assign'} on all FBs I want to REFERENCE TO them. Someone always uses := instead of REF= and this attribute fixes that.
Good find for solving the pointer/opcua problem!
Hi there, We have a German machine with an Eaton XC-202 plc. I purchased the X-soft CoDeSys software and XT-SUB-D/RJ45 cable for programming...
4,068
Hi Siemens guys! I am experiencing SF fault on our S7-300 (6ES7 315-2AH14-0AB0) CPU from time to time. I've checked the diagnostic buffer and...
184
Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
89
I have to provide remote access and control to a touch screen. I was thinking about using Weintek and the Weincloud. Does anyone know if this is...
614
Greetings, I am working on a project and I would like to scale %AI to -10.0 to 10.0 VDC. The module Input data is stored as a 16 bit Integer and...
75