How to Connect RS422 to Laptop?
samadrazm
Nov 2011
Here
31
Does someone know how I can I connect RS422 port to my laptop. There are adapters to do so, but they are quite expensive. Is there anyway I can build the adapter by myself?
PS: The RS422 interface is located on a serial module (CP441) on a rack with Siemens S400 series CPU. The interface is used to connect a weigh scale to the PLC. But I cannot get the communication to work. So I am trying to connect it to my laptop for fault finding.
Any suggestion.
Thanks,
Samad
Both RS422 and RS232 are serial.
I have serial comms on my laptop but it is RS232, I need to connect to RS422.
What is it you are connecting to? if its the 400 why dont you use a MPI, the GE cable will not work on a Siemens PLC
The thing is I have trouble to connect a CP441 to a weigh scale using RS422.
I want to connect my laptop to the serial CP module and see if I can send o receive anything. It is purely to test my program and if the config and connection I have made are correct.
Do you have a scope ? if you know the pins you are writing and reading to/from you should be able to see it
Hi everybody! Im meet a big problem that my PLC is FX1n 24Mr and he has an Rs422 Com port, and the HMI is Delta TP04P series has Rs485 2w...
2,453
Greetings, I had an issue with a RIO rack 2 and IFM I/O Link dropping on my network. I would loose connection for a second or 2 then they would...
90
Hi friends, i need a help to know the procedure and steps to connect Lenze i700 to PC for parameterize. i tried with lenze easy-starter using LAN...
50
Hi, We have been facing a issue with SCADAPack 474. Configuration is like below. RTU 474 + 6103 PS + 5606 IO Mix Module + 5414 DI Module Only...
73
363