How to move number 4 in to Counter

You don't have a PV value defined, so it is probably defaulting to 0.

You seem to have I3.0 on continuously. This means the counter is going to overwrite the CV EVERY scan.

If you want the count to activate on a transition, you need to put a One-shot on your I3.0 signal.

In the "bit logic" menu look for the symbol --(P)-- and read the help file for how it works.

Declare a variable for the PV of your counter.
 