How To Protect 120VAC PLC Input?

Thanks Stationmaster. That's a big point!
Connecting caps or MOV's across motors may affect their operation. I expect the spike is during turn-off, so an MOV may be okay.
The best choice is still a relay - either mechanical or SSR.
Because they are just sensing if the motor is on, a current sensor would also be a good suggestion.
 
Agreed. I see kittydog42's problem. How do you call it a design problem if it worked for 10 years? We all agree there is a problem with the design.
The Nano manual listed the AC input as 'Capacitive'. I wonder if they have a series capacitor inside. You only need 10 mA to turn on the input. A series cap would also work, and limit current. Anyone care to calculate the value? My guess is .22 MFD, 400V.
 
Following up six years later. I ditched the Automation Direct DL05 PLCs and switched to GE VersaMax Micro. No issues with direct 120V, just like the Nano. Eventually switched the GE for the Micrologix 1100, also no issues. The Automaton Direct units were just not very robust. The irony is that I wasn't buying it due to the low price, it was the one of the only 120V PLC with 120V inputs I could source to replace the Nano when Schneider discontinued it.
 

Similar Topics

Hello Everyone, I have in an electrical panel a simple 220VAC to 24VDC power supply (as shown on the picture bellow) can this type of power...
Replies
6
Views
1,364
Hi, I recently had to buy a batch of new electrical components containing 10 PLC Omron Type (CP1H-X40DRA) Apparently stored in store (to be used...
Replies
10
Views
3,569
Hi, I'm currently in the process of locking down a program, I have managed to set passwords for FB's and WS but can't seem to find a way of...
Replies
10
Views
1,785
Hi I'm trying to re-program a Mitsubishi FX0-20MR-ES plc but when i Initiate transfer from GX developer it keeps asking for an 8 digit Hexi...
Replies
1
Views
2,102
Back
Top Bottom