How to reset a 1734 Generic ethernet module via MSG

dmbartender

Member
Join Date
Jul 2008
Location
Germany
Posts
40
Does anyone know how to do this via MSG or SSV? All I want is the "Reset Module" type of command that one can find in the third tab of the generic module properties.

Thanks ahead of time for your consideration!
 
The CIP Generic MSG type includes a "Device Reset" as one of the function codes (CIP Service code 0x05, Class 0x01, Instance 0x01, Attribute 0x00).

Experiment with this function carefully. Some devices perform a soft reset (like a power cycle) and some actually perform a factory default parameters reset.
 