How to send more than 127 chars through 1734-232ASC?

asteroide

Member
Join Date
Jul 2010
Location
der
Posts
158
Hello Friends

I have took the sample program from AB webpage and modified, but I can only send 127 chars.


I need to send like 250 chars to a printer Zebra. How can I do that?

Thanks in advance
 
The 1734-232ASCII has only a 128 byte buffer.

If you need to send more than 128 bytes, you'll have to break it up into frames. As long as the Zebra isn't too sensitive about inter-character pauses during a string, that should be straightforward.
 