how to take the data from level transmitter to analog input omron?

kartika

Member
Join Date
Jul 2011
Location
Lampung
Posts
31
hi all...i'm still confusing about scaling in PLC..need ur help, please..
i have a differential level transmitter, the signal is 4-20mA,and analog input Omron CS1W-AD161-V1 (16input channel), how can i take the data from the level transmitter to the analog input?
thanks for the attention
 
thanks for jvdcande, but would u like to explain more to me, because i'm still confusing about it...
i read that it just MOV the data from sensor and then transfer it to memory, is my opinion right? do i need another instruction or just MOV and transfer it?and how can i set the data that say 4mA is 0% and 20mA is 100%...?
best regrads..
 
The raw data will be the allocated input channel.
You will need to review the W345 manual. It will explain where the data will be based on the Unit Number of the module that is set on the two rotary switches on the front.
You can scale the raw value with the SCL instruction.
This instruction is explained in the W340 manual.

Hope this will help.
 

Similar Topics

hi all...i'm still confusing about scaling in PLC..need ur help, please.. i have a differential level transmitter, the signal is 4-20mA,and...
Replies
0
Views
3,116
Hi guys I have Productivity Station which will collect Run time data from Phoenix input block "ILB ETH 24 DI16 DIO16-2TX". I am new to crimson...
Replies
0
Views
2,923
Hello. I have a db which is 1000 INT, and this db is represented in WinCC as a raw data type set of 5x 400 Bytes. This set is read with a script...
Replies
1
Views
65
So i've been at this for a long while, i have Citect Scada 2018, i have full access to everything but i can't seem to find any option or...
Replies
0
Views
58
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
164
Back
Top Bottom