How To Tune Pid For Tank Control In Rslogix 500
siva_maddala
Apr 2006
BOMBAY
63
Hai welcome to automation world
recently i am working on MICROLOGIX 1100 i did the operation for PID block. that is one tank is there and one inlet modulating valve is there so i have to control the valve using level of the tank. i created PID block and checked in manually it is working nicely whenever it is in auto suppose if the setpoint of tanklevel exceeds the level of the tank then valve is auto matically opening suppose then we reduced the setpoint to below the tanklevel then valve is not closing still it is opening, i set the parameters are
proportional gain 1
ti 1
td 0
E = SP-PV
TIMED
YES
DEAD BAND 25
SO IF ANY ONE KNOWS THE VALUES HOW WE HAVE TO SET IN PID BLOCK FOR MICROLOGIX IN RSLOGIX 500 Immediately send to my mail id. i am eagerly waiting for your reply
thanks and regards
M.SIVA
I do not know how your valve reacts to the signal being sent to it.
Look into the following
Could it be that your E=SP-PV is incorrect
Maybe your loop is poor tuned so the integral windup is creating this reverse valve action.
When you switch to manual normally you can switch the PID block itself to manual to prevent integral windup, see Bump less transfer in help. Off my head I can’t remember it exactly.
It is now an add on license option for $ 713 After a week of nobody @ Rockwell being able to tell me why my Auto tune was grayed out... I...
33
11,157
I am troubleshooting a PID loop developed and tuned by others. It is a heat exchange process, utilizing steam and control valve to heat up process...
21
6,433
Hi I'm working with twdlmda20drt twido PLC. I can work with the pid but i can't work with autotune, i read the whole instruction sheet but it...
2,497
When I tried to use the autotune feature, my CompactLogix complained that the input was not stable enough prior to the step change. I had to tune...
1,946
hi everyone i have cpu 224-Xp and tp177b pn/dp color. my customer wants to autotune the pid form HMI. i have defined the table as given in the...
1,841