Humidity Monitoring in Hazardous Area
DaveW
Apr 2005
SoCal
389
Looking for a way to monitor humidity in a Class 1 Div 2 area using wireless, battery powered, and a laptop to log data. Any recommendations? I rather not use a PLC becuase they want to be able to move the transmitter around to different areas.
Joe, thanks for that video. How are to talking to the Red Lion? Does the wireless need line of sight?
DaveW,
No it is does not have to be Line of Sight. It can penetrate walls pretty good. Pine trees seem to be it's Cryptonite. So is a mound of dirt.
Back at the Red Lion unit we have the Banner Engineering SureCross that talks Modbus485 directly to the Red Lion unit. If you really wanted to use a PC to do the logging, you use Banner's GatewayPRO model which is a node on ModbusTCP. Then have some software running in the PC that would talk to the GatewayPRO. This route may not be as easy to accomplish as the other idea.
Here are some other examples of the wireless being used in plants where it clearly is not Line of Sight.
In this video and about 2minutes into it we are temporarly mounting the RH node. It also reads Temp as well.
http://www.youtube.com/watch?v=-nGGkLFZPFs
In this video we are conducting a Site Survey at another plant location.
http://www.youtube.com/watch?v=D13_Gil90AE
Both of the installations take the data and import it into Pi Historian directly.
Joe_WaZoo
Joe,
ModubusTCP will probably work for me. I can get Wonderware to poll for the data. Thanks again.
Getting intrinsically safe or rated for Cl 1 Div 2 equipment may be difficult and expensive.
It may be easier and less expensive to have all monitor equipment outside of Cl 1 Div 2 area and run a tygon tube into the area to get your reading. If you are looking for a real short term spike transit time of the "spike" may be a problem. If conditions are fairly steady state transit time in teh tubing may not be a problem.
Depending on length you may need a pump with high dP to get your sample and then tee the discharge to tap into line for instrument. Many of the pumps used in industrial hygiene are rated for use in combustible atmospheres but they are not cheap either. Battery powered units will run for 4 to 5 hours reliably.
Why are you doing this?
Dan Bentler
Dan, I like the Tygon tube idea. QC wants to monitor some of the rooms and dryers where we are making our product. The want to be able to move the transmitter around so anything fixed or bulky won't work.
Thanks,
Dave
Thanks, Dave
Dave
Sounds like workroom air monitoring for employee protection.
Direct colorometric tubes may be an option for quick spot checks. Pump alone 3 t0 500 tubes 5 to 15 each, have limited storage life.
Right up my alley and expertise area ie industrial hygiene and electrical.
IH for rent -- have pump will travel.
Dan Bentler
I am looking for temperature/humidity sensor recommendations. Would like the sensor to display temp and humidity. Need to connect to a Contrologix...
236
We've had a number of design discussions and done some extensive testing on enclosure heating/cooling solutions for various panel builds...
696
For you instrument people. I'm using a PLC, VFD, and HMI for climate monitoring and control. Automation direct has combo Humidity and Temp sensor...
2,026
Does anyone know of a sensor/transmitter that is able measure humidity/dewpoint/water concentration in a stream of 1200F air?
3,436
Hello, Has anyone developed the relative humidity value by a temperature thermocouple? I also have pressure values. I have seen some formulas to...
1,981