Not it is not. If you took the time to read the original post, you would have seen he has ruled out a phase relay.

I did read it, i discounted it as a comment from somebody who has not actually used a phase failure relay before.

If that won't operate in certain circumstances then what difference is a relay going to make ?
 
Last edited:
I agree with Bryan on installing contactors so if a change is required and voltage from another source is applied the other source has been removed such as with a house generator, this way you wont get backfeed. To monitor with a relay use 2-220 vac relays L1-L2 & L2-L3 won't let a single phase occurrence trick you. Just a thought
 
This thread takes me way back to when I first started in the industry


VERY NICE!!! :ROFLMAO:

I remember the old timers talking about 'the way it was', when I first started out I worked in a printing plant... over 1 mil sq feet, they moved from San Francisco to Newark and they were always talking about the 'old plant' it was the clock tower, they had 4 buildings in downtown SF and the rigging they had to do back then was amazing, most of the guys I worked with started there in the 50's and not much was electrical, they had one printing press that was just about all mechanical and it was a piece of art.... 3 stories tall and about 60 yards long, it took two days to do a lube job

The clock tower is now housing https://www.youtube.com/watch?v=Atqva_5ApzY

One of the helpers I worked with had to go up and oil the clock every day, I think he just loved the views :)
 
Three relays put in delta on your phases or in star to the neutral. Take one contact of each and put these in series: indication that all three phases are on (1 on PLC input). Take another contact of each and put these three in parallel: indication for all three phases off (0 on a second PLC input). Both inputs 1: everything OK and power on. Both inputs 0: everything OK and power off. Any other combination: check out things before switching.
 
I reviewing this post I just realized something
We are talking about a 3ph motor moving cars with the power source coming from 1 of 3 different power sources. As we all are aware that 3 phase motor rotation direction is dependent on the supplied power sequence. So just knowing if the power is present is not enough you also need to phase match all 3 power sources in order to ensure that the motor run the intended direction no matter which power source is used.
While it in possible to design a DC power source that could connect to all 3 power sources. In face they could all be connected at the same time the dc output would be powered from whatever source has power at the time somewhat like as UPS system.
With an AC power source it can be dome but the 2 generator sources must be synchronized to the AC line source in order to work. This same thing is done with every power station that is connected to the grid.
If you setup a system the used multiple power sources and disconnect one and then connect another it could cause an unexpected reversal of the motors putting personal at risk.

As solution that may work would be to control all the motors using a VFD connected in a common DC buss configuration. Each power source supplies power to the DC buss while connected.
If all the power sources are at the same voltage the buss would not care what the source is.
This would simplify the controls and eliminate the power source problem.
 

Similar Topics

I have an old Sentry Palletizer (S/O Number 3007 / Serial Number 1172) that has lost its program as the backup battery died years ago. I can...
Replies
0
Views
97
So i've been at this for a long while, i have Citect Scada 2018, i have full access to everything but i can't seem to find any option or...
Replies
0
Views
67
I've got this 3-phase 575V motor that we're controlling with a VFD (Variable Frequency Drive), which has been quite the learning curve in itself...
Replies
10
Views
309
I'm fairly new to Rockwell software, I've had some basic training in the past but nothing too advanced. My company and I use Reliable products for...
Replies
11
Views
374
Hi all, I am having issues accessing my Cimplicity software - the site code changed after re-install and I am no longer able to attain a new key...
Replies
10
Views
194
Back
Top Bottom