if we upgrade the plc to another brand
lmqvip
Jun 2005
We change PLC fr. simens S5 to Ge fanuc.
can I copy my s5 program in LAD representation into GE directly , and just redesign the operands again.
like put the flowers in a new vase.....
does it work?
There is no program that will convert the S5 files to whatever files the GE requires, you will have to input the program manually into the GE. This should not present you with any problems if it is only ladder that you need to convert.
Paul
Paul,
I wouldn't be too sure about having no problems. Just think about the different way latches are programmed: latch and unlatch (Allen-Bradley), keep (Omron, set and reset (Siemens and several others). Also retention can be a real problem: is it the instruction (Allen-Bradley) or the memory location (Siemens) that determines retention? I agree that the are not mountain-high, but they still exist. Besides that I dn't know in what bin the GE Fanuc falls exactly.
Kind regards,
Interesting analogy...
Depending on the size/complexity of the bouquet, you will definitely need to rearrange the flowers...
Some flowers will need to be exchanged for different varieties, though you should be able to produce the same aroma in the end...
-Eric
-Eric
AWWWWWwwwwww, that is so beautiful. :cry:
Erics right.
You have to print out the program from the old plc and interperet it for the GE and then manually re-enter it into the GE.
If you have a large program, it's going to be a long haul.
Casey, as a matter of fact YES. China is on the west bank of the St. Clair River just downriver from Port Huron. If your in the neighborhood stop in at the Marwood bar.
Hello all, I have a one problem. I would like to upgrade Mitsubishi PLC Q02 to Q03UDVCPU. I have Q02 program and I change to PLC type and try to...
159
Hi everyone, Kind of new at this, so we recently upgraded our 1769-l32e to the newer 5069-L320erm, i converted the file over and Verify the...
417
I'm involved in upgrading an IDEC FC5A-D12S1E PLC to a FC6A-D32P3CEE. I've attached the original layout of the system. Since then, another HG3G...
449
Hello, I've recently tried to upgrade my PLC controller from a L72 to L84ES and everything seemed to work, all buttons and screens as far...
2,642
Hi, we are using 1756-L61 PLC redundant system in one location . due to some minor faults , we upgrade the firmware from 19.52 to 20.58. after...
1,343