Incremental encoder signal duplication
SDC22
Aug 2015
Michigan
I am looking to duplicate a quadrature encoder signal where the original supplies a VFD and the duplicate goes to a PLC. I have had success using a signal repeater in the past. I'm wondering if anyone has tried to simply parallel wire the signal inputs?
The encoder has a current limit. Adding a parallel device increases the required current. You could be OK as long as the current draw does not exceed the rating of the encoder. Add up the current draw for the PLC input and the VFD input and compare to the capacity of the encoder.
There's also the added capacitance that can cause havoc on encoder signals, whilst a repeater will (generally) reconstruct the signal to make it square again before outputing.
Are the VFD and PLC input circuits even the same type (Single-ended, push-pull, differential) ?
Are both the VFD and PLC input circuits isolated from the rest of the controller, so you can connect together the DC Commons without causing interference between all the other I/O circuits ?
Unless the answer to both of those is "yes", I would recommend sticking with the isolator/repeaters that work for you.
I have an application using an incremental encoder and then I convert it to degree (0-360) using calculation program. For a while, the calculation...
328
Hi all, I am using a B&R X20 unit and want to integrate an incremental encoder (OUT A, B, & Z). I have three BOOL digital input pins for my A,B...
458
A bit of background here: We use an incremental encoder with a counting module in our PLC configuration. Using dual phase / quadrature counting...
26
8,988
Hello, I am trying to take the counts I am getting on my plc from an incremental encoder and use them to keep track of position. I have never...
1,330
Good Afternoon , We are thinking of using a BEI Incremental Encoder for one conveyor control , but keeping track of the speed of this...
1,725