Inovance PLC

Join Date
Jun 2013
Location
Jaipur Rajasthan
Posts
18
Hi
I am using H1U-1410MT Inovance PLC.
I want to read Flow meter reading threw MODBUS and then send data to BMS using same MODBUS.

Can somebody help.
How can I do??

Please guide
 
First of all, that PLC is another clone of the Mitsubishi FX series probably FX3U
In the IDE (Autoshop) click on the PLCParameter in the project tree & set up the com ports Com1 & 2, you need one of them to be a master station i.e. either the PLC, the flowmeter or the BMS.
Set the parameters.
In your program, you need to call a function called Modbus (these are also in the project tree as an instruction), if you highlight it and press F1 key it will bring up the help file for that function. There it gives you a little bit of information but not much, I suggest you go to the mitsubishi website & search for the FX modbus communiction manual, they use ADPRW function that is the same as the MODBUS function.here is the manual

https://dl.mitsubishielectric.com/dl/fa/document/manual/plc_fx/jy997d26201/jy997d26201g.pdf

Modbus.png
 

Similar Topics

good day I have an Inovance H5U plc that is password protected and I want to use it in another application, only it doesn't allow me to download...
Replies
0
Views
598
:cool:Dear Superiors, I have an inovance VFDs and they give ERR 24 time to time.I read the manual and i couldn't found what is that error 24...
Replies
0
Views
1,411
Hi, I am trying to set up a plc. I've never done any programming with ladder logic previously. I'm trying to set up a a program to turn a device...
Replies
6
Views
116
Hello, I have a question about an encoder that has absolute measurement. Specifically, it's the Lika SMA5, which I would like to connect...
Replies
2
Views
53
Hello, I have a question about an encoder that has absolute measurement. Specifically, it's the Lika SMA5, which I would like to connect...
Replies
0
Views
30
Back
Top Bottom