Instrument cable
Lc1
Jan 2014
Uk
59
Hello,
I have a question regarding instrument cable. I know that for 4-20ma transmitters twisted pair cable should be used with the screen grounded at one end only. However for digital signals ( limit switches , push buttons ) can 2 core/ part of a multi core cable be used ?
Thanks for this. Am I correct in that noise will not impact a digital signal as much as an analogue and that is why cores can be used instead of twisted pairs.
Thanks again
Thanks again
Of course, one can always find an exception to the rule, but generally speaking, that is correct. I little bit of electrical noise will not typically cause a false reading on a discrete input.
This is one of those "it really depends..." kinda answers.
In a reasonably low noise environment we do this often.. one 24V supply out to an instrument with multiple digitals, the inputs come back on various cores in the multicore. No problems.
But in a very noisy environment, you want to take advantage of the common mode cancelation provided by a twisted pair. Squirting a lot of noise back into your DC PSU isn't ideal. If your cable has to run close to large cables from noise generating things like VSDs, motors, switchmode power supplies etc... then use one twisted pair per digital.
If you use individually screened pairs then i have no issue with mixed analogs and digitals in the same cable.
consider cable routing also so 4-20 signals are kept away from vfd and motor cables
hi all what is suitable shielded cable for connect pt1000 sensor to plc .? (50 meter distance . plz tell me all layer for example cu/pvc/pvc )
1,517
hello fnds wats the difference betwen instrument cable and control cable regards jos
3,716
10,800
Hi all, Looking for a temperature sensing solution for determining ambient temperature in the frigid Canadian winters. Discrete outputs are fine...
1,508
I was tasked with putting together equipment for a mobile temperature monitoring system for our oil rail cars. Apparently, the crew that unloads...
841