instrumentation control pilosophy
Off the top of my head, instrumentation philosophy might include things like
- analog 4-20mA to include NAMUR level fail-safe/fault indication
- analog inputs configured to read NAMUR level fail-safe fault indication
- series diode to be installed (at wiring terminal location) for each 4-20mA loop for current loop check
without breaking the loop
- HART protocol to be specified/used/purchased when available
- specification for a fieldbus protocol (Profibus, ASI, Foundation Fieldbus) for instrumentation
- limitations on technologies:
- ultrasonic level technology for open channel flow only, no covered tanks or pressure vessels
- standardized hazardous area technology: EXP vs I/S (containment vs energy level)
- remote capillary seals as last resort for gauge or DP measurements
- use of crimp ferrules, or not
- location of instrumentation transformer (with a view to regulations involving arc flash)
- whether the presence of fluids other than instrument air in a control panel is permitted
- standardization of engineering units, like temperature, pressure, flow
- Ban on materials that are detrimental to a process (brass for ammonia, silicone in the automotive field)
- handwheel on valves
- tag format
the list is by no means complete, it's just off the top of my head at lunch time.
you wrote a statement, not a question...
you might want to explain what you need it for, what are you trying to do?
That is why the question marks - no detail as to what you require.
OK now I have to ask. Did Badger really give dginbuffalo a yacht? and what's the ETA from the UK to Buffalo, via the pond, St. Lawrence then to Lake Erie I guess
my two cents worth
. . that series diode is most useful, but I am adding to the thread to promulgate an old navy saying...
. . the only constant is the varying rate of change.
bill
Hey guys! I'm a newbie in the control area, so I'm gonna drop some thoughts here... We want to control the opening of big silos (about 1900...
1,494
Hi, Just wanted some thoughts on protecting control and instrumentation from welding damage. We had a PLC and drive fail after some welding work...
5,003
Following on from the recent thread about using a PLC for furnace control, this has me thinking about a potential future project. I have just...
5,026
Any recomendations for a good instrumentation books. I have realised that programing without the knowldge of everything else around is not very wise.
2,453
Hi all, I want to know what kind of instrument cable (4-20mA signals) between Control room and field instruments in temperatures up to 50oC...
4,288