Just exported a working FB to an external source in Tia v13. Tried to import it by generating the source in Tia v14 and the block cannot be compiled in Tia v14 ???
Any ideas ?
Thank you,
Kind regards,
G
DPRD needs the LADDR as a HW_IO data type - I noticed that the type checking has been tightened up from V13 to V14
Plus, the HW_IO is not the peripheral address, you need to use LOG2MOD on the address to get the HW_IO.
(found this out using a 1517 CPU)