Raffe Member R Join Date Apr 2017 Location Sweden Posts 26 Jun 1, 2017 #1 Hello all, I need your help! I'm new to InTouch. If I would like to read from a S7-300 PLC, if I would like to read DB1.DBW0 how do I define that in the tagname directory? Please help! Raffe
Hello all, I need your help! I'm new to InTouch. If I would like to read from a S7-300 PLC, if I would like to read DB1.DBW0 how do I define that in the tagname directory? Please help! Raffe
userxyz Member U Join Date May 2002 Location any Posts 2,768 Jun 1, 2017 #2 Dassidirect Have you installed the DASSIDIRECT driver from Wonderware ? https://www.logic-control.com/media/DasSIDirect.pdf kind regards, G
Dassidirect Have you installed the DASSIDIRECT driver from Wonderware ? https://www.logic-control.com/media/DasSIDirect.pdf kind regards, G
Raffe Member OP R Join Date Apr 2017 Location Sweden Posts 26 Jun 1, 2017 #3 Hello, Yes. Is this the correct notation for the "Item" in the Tagname directory DB1.DBw0 ? Regards Raffe
Hello, Yes. Is this the correct notation for the "Item" in the Tagname directory DB1.DBw0 ? Regards Raffe
userxyz Member U Join Date May 2002 Location any Posts 2,768 Jun 1, 2017 #4 No No, Item: DB1,W0 Accesname is correct ? Kind regards, G Raffe said: Hello, Yes. Is this the correct notation for the "Item" in the Tagname directory DB1.DBw0 ? Regards Raffe Click to expand...
No No, Item: DB1,W0 Accesname is correct ? Kind regards, G Raffe said: Hello, Yes. Is this the correct notation for the "Item" in the Tagname directory DB1.DBw0 ? Regards Raffe Click to expand...