The reason why we want to run with the 1-phase inverter is because we want to have the possebility to install the lift in places were 3-phase is not available.
DickDV, about increasing the tourqe limit,,
Actualy the inverter is oversized for the motor. So we have a 2,2kw inverter and a 1,1kW motor. When we run the motor on the 230V inverter the motor runs fine up to 50Hz, after this the current starts to rise and when we get closer to 60Hz, current starts to rise very rapidly and motor starts to stall and then stop, at this point the current is very high for the motor but the inverter has more current to give. We never get any alarm from the inverter!
Kalle, your point about field weakening area is very interesting. I am going to look into this further.
Maybe it is a combination of different cases;
1 Motor has a little bit less tpourqe at rated speed Star connection
and not sized with any margin (DamianIn)
2 Inverter comes into field weakening area with the 200V inverter above 50Hz
For info: inverter has at the moment only been tested in V/F mode.
We will try to do some testing in open loop vector and see if there is a difference.
If any one has more info about the phenomena that the tourque charasteristics are differént in star/delta connection I am happy to listen.