Is OPC DA Win7 client, Win10 server possible?

patjdixon

Member
Join Date
Nov 2018
Location
Lago Vista, TX
Posts
63
I have a Win10 64 bit host for my OPC DA server, which is Indusoft (Studio,Scada.OPC.3). Locally OPC works, Matrikon OPC Explorer. On my Win7 client I can ping the host and the OPC test client finds the topics, but I either get access denied or topic not found when I try to connect. I have tried everything I know of, including info on these links, to open it up and get it working.

https://groups.google.com/g/op.....Ud5Q?pli=1

https://www.aggsoft.com/opc-da.....nfig-4.htm

https://honeywellprocess.my.si.....0is,system) to connect to it.

https://support.languard.gfi.c.....e-Registry

opc_acess_server_system_2023-08-03 at 8.33.47 PM.jpg opc_acess_server_comm_2023-08-03 at 8.28.36 PM.jpg opc_acess_client_findservers_2023-08-03 at 8.30.00 PM.jpg opc_acess_client_io_access_2023-08-03 at 8.35.21 PM.jpg opc_acess_client_seesopc_2023-08-03 at 8.31.19 PM.jpg
 
I've been browsing the forum for another OPC related topic and found this unanswered question. I know it's been years :) but just in case someone else is having the same problem. This is an issue related to DCOM configuration. DCOM is required to enable remote communications for OPC Classic components. DCOM configuration guidelines are available for download here.
 
Newer windows have more and more Dcom settings disabled for security reasons by default. User name must match and even after lot of editing DCom settings it still usually won't communicate to another PC.
 
DCOM has always been messy, but relatively recently Microsoft added security patches to Win 10 (for good reason) that pretty much broke everything.


Most vendors took the approach of "you know what we mostly switched to OPC UA a while ago, there are few enough customers using the old OPC protocol that also are using up to date windows that we're just gonna focus on the new and let the old fade into oblivion".
 

Similar Topics

Here's the situation...I'm upgrading an old computer that had been running Windows 98 to Windows 7-64bit. I have no choice in the computer...
Replies
20
Views
7,410
I am running CCW 13 trying to upload to a micro 820 vers.12 I get an output message OPC server is unable to load project controller. Please help!
Replies
5
Views
235
I know nothing about simaticnet OPC server. I do know Kepware. I would only ever scale raw to engineering in the PLC, but it is possible to scale...
Replies
5
Views
219
If anyone has a crack for IBH OPC Server, please send it to: [email protected] Urgently. Thanks in advance!
Replies
1
Views
131
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
Replies
1
Views
182
Back
Top Bottom