Or there is an alternative to this? I suppose there are many but I've only seen put/get
Can you for example set up a new plc and connect it to an existing scalance or profibus node, and have both PLCs read the same inputs? Or for example have one PLC raise outputs as signals to the other PLC?
You can, and should consider, multicasting when you have a large number of controllers as well.
Also, if you use PUT/GET, you must have some sort of heartbeat to detect if the other end is actually processing logic or simply turned on but in stop mode.
What is your PLC and FW and SW version?
Current Siemens PLCs support controller to controller comms as IO: I-Slave on Profibus, IDevice on Profinet. As you suggest, it maps IO memory in one PLC directly to IO memory in another PLC.
There is also a feature for multiple PLCs to read the same inputs from an IO rack, called MIMO, I think? It requires the IO device to support it, and not many do.
I have a project in panelbuilder32, and I want to put a password to secure the project from uploading to other people computers
80
Hi looking to install a smaller less sophisticated PLC for fountain timing and also one analog pressure sensor which would be used to detect...
23
639
Hello All, After trying to transfer some field changes on the safety scanner microscan3, and verifying, the device is stuck at .... waiting for...
124
I have a 120V relay, 120V DI card and a analog input. I was wanting to know if i could put a 24V DI and well as a 120V DI card on the same plc...
111
Hi There, I have a filler with a coriolis flowmeter that has died. the filler requires a pulsed output (manufacturer wont edit the program) is...
290