Issues after changing from 1769-OF8 to OF4CI

ceilingwalker

Lifetime Supporting Member
Join Date
Mar 2010
Location
Phoenix, AZ
Posts
1,589
Hello all. I switched the module for a CpLX rack because we don't have a spare 8 chan module (1769-OF8C) and have a line down. We only use 3 channels and we do have a 4 Chan module that I am trying to swap it with to get this line back online. Whilst verifying the project, this alarm comes up:
Capture2.PNG

When I cross ref this, this is the only place it is used in the project:
Capture3.PNG

......and this is the actual code:
Capture.PNG

I can't understand what the issue is? The data type is appropriate for this module. Any help would be greatly appreciated. Thank you
 
I found the solution and understand it as much as I understand the original problem. I deleted only one of the OREF's and used the exact same tag it was pointing to before and that made all my errors go away.
 

Similar Topics

Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
Replies
8
Views
241
Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
Replies
5
Views
197
I'm at a loss here and hoping someone else has seen this: Background: We've got two identical machines on our floor (we'll call them machine A &...
Replies
0
Views
85
I have an Allen Bradley temperature switch that I am trying to use in studio 5000. I am getting the message "Unable to interpret the IODD file"...
Replies
0
Views
109
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
7
Views
298
Back
Top Bottom