Hey Guys,
I have an Keystone 051 modulating actuator that I control through Allen Bradley Compact Logic PLC, this actuator is connected to a butterfly valve

I need to make this actuator open slowly, I have contacted the manufactor and looks like I can change this to 38 secs/90°

Is there a better way I can control the speed of how fast this actuator opens this valve in the PLC? I dont want someone to slam this valve open because this is whats currently happening.

Thanks alot
 
If the voltage to power the actuator is 100 to 240 VAC, you can use a soft-starter to control the ramp time.
 
Valve operators often move too fast for my applications as well. I used to order 60 seconds per 90 degree travel, which was usually fine. I used Auma and RCS operators, which could be ordered that way.

You already have the operator, so you are stuck. The best approach is to use a ramp function for the analog signal to the valve. One way, not the most elegant, is to use a resetting timer, say 1 second, and increment or decrement the signal by 0.25 mA (16/60 = 0.27). Keep doing that until the feedback signal or the output signal reach your desired position.

One caution - the Keystone actuators I've used don't have a brake. The motor tends to "flywheel" after the contactor opens, causing some overshoot. This can interfere with accuracy.
 

Similar Topics

Hi I am beginner and I need to interface LCD to option board TA5141-RS232l-- I have PM5052-T-ETH. Can somebody guide me how to start- and complete...
Replies
0
Views
341
Dear All, Is there any way to communicate the weintek HMI (simulation) with RS emulator 500 logic. No hardware available PLC/HMI. I want to test...
Replies
1
Views
1,743
I know this may be a little off topic, but Im having a little issue with a Rosemont level transmitter. The only info I have on the device is when...
Replies
15
Views
4,290
hi all, i need to know that "are this transmitter convert the measured diff. pressure value to level value or how i can convert it as plc have...
Replies
4
Views
1,497
Hi, Rosemount's 2051 documentation (like the Rosemount 2051 Configuration Data Sheet, 00806-0100-4107, Rev EA available at...
Replies
15
Views
4,490
Back
Top Bottom