Kinco HMI connection with Mitsubishi FX1S PLC

MohsinJahan

Member
Join Date
Aug 2018
Location
USA
Posts
3
I am trying to connect a Kinco HMI (T070) with the PLC of Mitsubishi (fx1s) but I want to know how can I add PLC tags to HMI Buttons (when I will touch on button on HMI, PLC switch X0 should be energized). Can anybody here help me?

If I elaborate my question, I am simply asking about how to connect HMI tags to PLC Elements?

http://tiaportal.weebly.com
 
X0 is a PLC digital input, if the HMI forces its state probably it will not change.

You better use an internal bit like M0 instead X0
 
Sir, I do not know where should I write the address "MO" in HMI. For example I am using a toggle button and i design and placed it. Now there is no place to put the value/address in Kinco HMI software (as we have in Siemens HMI software).
 

Similar Topics

Good Day to all of you, this is my first post, i will try to explain as best as possible, english is not my natural language. I am performing an...
Replies
0
Views
42
Hi, Its possible communicate between kinco hmi (mt4404t) and Micro830 through a serial line ( rs232/485 ) ?
Replies
2
Views
1,562
Can anyone help me getting this communications connection set up between KINCO GL100 and KINCO K508-40AR? I am using Port 1(RS485) on the KINCO...
Replies
1
Views
3,312
Hi all. Are someone was tried to connect HMI with only serial port ( rs232/485 ) to a PLC (S7-1200 + CM 1241 RS485 ) I have a machine, where is a...
Replies
0
Views
1,247
Does anybody have experience with the data logging on a Kinco HMI? I'm currently trying to log some dumb data. I have already created the DB and...
Replies
0
Views
1,089
Back
Top Bottom