L83ES processor and SERCOS
infer
Feb 2021
UK
Hi all,
My first post 🍻. I'm Jay from the UK.
We are in the process of upgrading our hardware to 1756-L83ES, most of our lines use motion drives over ETH/IP however we have 2 lines with DNET and Kinetix 6000 / SERCOS.
I have zero experience with SERCOS, however I was hoping it won't be complicated. Sadly I was very wrong.
Going to merit:
Plant ran on L72E v28.011 , 2x M16ES and 12x Kinetix 6000 ring.
I have flashed sercos cards to v31 and pluged in L83ES, firmware, bootp etc all good.
I have then converted program to new version (31) and then changed the controller from L72 to L83es and downloaded.
All I/O are up and running but both sercos cards.
Status says Major Fault : Recoverable , Internal State Communication Fault, Configured No , Owned Yes.
every axis has.
Displays on the drives mostly spin and do not show anything, 2 drives have E75 fault , when I power cycle them the will go from 1 to 2 and back to 1.
As soon as I stick old L72 controller all works fine.
I'm completely lost
This is a known anomaly. Try the following: “Converting an existing project (non-V31) which uses the 1756-L6x or 1756-L7z controller to a project that uses a 1756-L8 controller, will not allow the sercos ring to phase up to 4. The drives will only reach phase 1 or will settle in a racetrack phase. To work-around the anomaly, export the L8 project to an L5K file, then re-import that L5K back to the ACD project, The drives should now reach phase4. (V28 thru V32 1756-L8 controller anomaly)”. This is from knowledgebase ID QA36075
Thanks for that! works :geek: Can't believe I wasted all day trying to find it :)
Many thanks again
Have a customer that has a running 1756-l83es, communicating to redundant ABCIP IO servers for Wonderware 2020. This configuration has been...
890
Hi, I have a machine set up with a L83ES and a ENBT/A Ethernet card in the rack. Ethernet card is connected to plant network. L83ES internal...
1,600
Hi, Is it possible to for an RIO with Flex 5000 series module, e.g. 5094-AEN2TR, to communicate with an 1756-L72E processor.
101
Is there anything I Should take into account while updating the firmware on a safety processor? I have a 1756-L61S running version 17 and need...
106
Hello all, I have been experiencing dropping network connections on the Co Pro quite a bit, 3 times a month. The remedy that we do to bring the...
760